1 AC Power For Business-Critical Continuity Liebert GXT T230 User Manual 10kVA, 50/60 Hz, 230V

2

3 TABLE OF CONTENTS IMPORTANT SAFETY INSTRUCTIONS INTRODUCTION AND SYSTEM DESCRIPTION Device Overview Options External Battery Cabinets Optional Interfaces UNPACKING THE UPS AND SITE PREPARATION Inspection Required Setup Equipment Unpacking Storage Handling Environmental Conditions Access required Floor/Rack Loading Inventory List Clearance Repacking the UPS INSTALLATION Electrical preparations Current Table and Suggested Cable Sizes Neutral Connection External Protection and Isolating Devices Installation of Differential Protection Devices External Electrical Connections Connecting Mains and Load Terminal Blocks for UPS Connecting Power Cables External Tower Batteries Connecting an External Battery Extension Battery Precautions Configuration Program Liebert GXT T230 Configuration Program Features What You Will Need OPERATION Normal Operating Block diagram i

4 4.2 Control Panel Controls and Messages Warning Indicators Fault Indicators Startup Preparations UPS Startup Procedure - Single Block UPS Shutdown Procedure All Ratings Maintenance Bypass Procedure Return from Maintenance Bypass Procedure Functional Test Remote Emergency Power Off Self-Tests Lamp Test Battery Test MAINTENANCE Testing, Replacing and Disposing of Batteries Easy Battery Replacement Storage Cleaning COMMUNICATION Communication Interface Port Terminal Block Any Mode Shutdown Battery Mode Shutdown On Battery Low Battery Liebert IntelliSlot Communication Cards Liebert MultiLink Remote Emergency Power Off TROUBLESHOOTING SPECIFICATIONS ii

5 FIGURES Figure 1 Liebert GXT T230 control panel 5 Figure 2 Liebert GXT T230 front and rear views 6 Figure 3 Unpacking 7 Figure 4 Standard configuration - differential breaker 11 Figure 5 Side view 11 Figure 6 Input and output connections with single source, single-phase input supply 12 Figure 7 Input and output connections with dual source, single-phase input supplies 12 Figure 8 Input and output connections with single source, three-phase input supply 12 Figure 9 Input and output connections with dual source, three-phase UPS, single-phase bypass input supplies 13 Figure 10 Hardwire terminals 13 Figure 11 Liebert GXT T230 with External Battery Cabinet 14 Figure 12 Overview of UPS tower 16 Figure 13 Control panel 17 Figure 14 System block, menu structure 18 Figure 15 REPO connections 24 Figure 16 Removing front panel and unlocking battery trays 26 Figure 17 Disconnecting battery tray and battery packs 26 Figure 18 Terminal block pin layout 28 Figure 19 REPO switch connection diagram 30 TABLES Table 1 Overview of UPS devices and batteries 6 Table 2 Connection data 9 Table 3 External protection device data 10 Table 4 Lighted LEDs 17 Table 5 Displayed text system block and main menu 19 Table 6 Warning indicators 20 Table 7 Display faults 21 Table 8 Battery test report messages 24 Table 9 Replacement battery pack 25 Table 10 Troubleshooting - errors and corrective action 31 Table 11 UPS specifications 32 Table 12 Environmental data 34 Table 13 Agency/safetycompliance 34 Table 14 Operating temperature parameters 34 Table 15 Typical battery run times, minutes at 25 C (77 F), 100% resistive load 34 iii

6 iv

7 IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS! WARNING Opening or removing the cover may expose you to lethal voltages within this unit even when it is apparently not operating and the input wiring is disconnected from the electrical source. Observe all cautions and warnings in this manual. Failure to do so may result in serious injury or death. Refer all UPS and battery service to qualified service personnel. Do not attempt to service this product yourself. Never work alone. This manual contains important safety instructions that must be followed when installing, operating and maintaining the Liebert GXT T230 uninterruptible power system (UPS). Read all safety, installation and operating instructions before installing or operating the UPS. Adhere to all warnings on the unit and in this manual. Follow all operating and user instructions. The Liebert GXT T230 is not intended for use with life support or other designated critical devices. The UPS is designed for data processing equipment. If uncertain the intended use for this UPS, consult your dealer or Emerson representative. This device serves as an uninterruptible power supply for connected loads. Maximum load must not exceed that shown on the UPS rating label. The device is in compliance with all relevant safety regulations concerning information technology equipment, including electronic machines for use in an office environment. Depending on the type and rating of UPS device, certain configurations of battery extensions may be connected. These battery extensions may be connected only to the compatible basic UPS unit.! WARNING Emerson considers the safety of personnel to be of paramount importance. For this reason it is essential that procedures relating to safety be studied before commencing work and properly adhered to thereafter. The user or operator may intervene in the operation of the UPS provided that the instructions laid out in Notes Regarding the EU Declaration of Conformity on page 3 are strictly adhered to. The installation of the UPS, described in Installation on page 9, may only be carried out by qualified technical personnel. Even when all switches and interrupters are open, hazardous voltages are present within the UPS; any operation that requires protective panels to be opened or removed may be carried out by Emerson authorized technical personnel only. 1

8 ! CAUTION Carefully read the following safety notices. Failure to observe the instructions may endanger your life, your health, the reliability of your device and the security of your data. Transport the unit only in suitable packaging (protected against jolts and shocks). If the equipment is moved from a cold environment to the operating room, condensation may occur. Before you switch On the equipment, it must be absolutely dry. An acclimatization period of at least two hours is required. The equipment must be installed in accordance with the environmental conditions specified in Environmental Conditions and in Table 12 - Environmental data. Even with all switches in the OFF position (see Figure 13 - Control panel) the UPS is not isolated from the mains. To isolate completely from the mains, the power cables must be disconnected. In case of interruption of the mains voltage, the integrated battery maintains the power supply to the user equipment. Lay all cables so that nobody can stand on them or trip over them. When connecting the UPS to the power supply, follow the instructions in Unpacking the UPS and Site Preparation. Make sure that no objects (e.g., pins, necklaces, paper clips, etc.) get inside the device. In emergencies (e.g., damaged case, controls or power cables, penetration of liquids or foreign matter), switch Off the device and contact the appropriate customer service representative. Do not connect equipment that will overload the UPS (e.g., laser printers or vacuum cleaners) or demand DC-current (e.g., half-wave rectifiers). When cleaning the unit, follow the instructions in Maintenance. The sum of the leakage currents (protective conductor current) of the UPS and the connected devices exceeds 3.5 ma for all ratings of the UPS. Earth connection is essential before connecting supply. Data transmission lines should not be connected or disconnected during a thunderstorm. Remote Emergency Power Off (REPO) input is located on the rear of the unit (see Terminal Blocks for UPS). When this connection is open, the logic circuit will immediately shut down the UPS output. An Emergency Switching Device (E.S.D.) must be fitted downstream of the UPS for the wiring installation safety to comply with the European Harmonized Document HD S1. Maintenance bypass switch is for the use of service personnel only. It is located under the rear cover. Open the safety cover to operate the maintenance bypass switch. The Tower UPS may be connected either to 3-phase mains or single-phase mains. Therefore the right input terminals have to be connected (see Connecting Mains and Load). The UPS autosensing mode ensures that it adapts to the connected mains supply. This equipment complies with IEC provided that the short-circuit ratio Rsce is greater than or equal to 250 at the interface point between the user s supply and the public system. It is the responsibility of the installer or user of the equipment to ensure, by consultation with the distribution network operator if necessary, that the equipment is connected only to a supply with a short-circuit ratio Rsce greater than or equal to 250. For three-phase equipment, the disconnect device shall disconnect simultaneously all line conductors of the AC mains supply. For equipment requiring a neutral connection to an IT power distribution system, the disconnect device shall be a four-pole device and shall disconnect all line conductors and the neutral conductor. 2

9 ! CAUTION Do not connect more than two Liebert GXT3-240TBATTCE battery extensions to the Liebert GXT T230. The vents for air intake and outlet at the front and rear side must not be obstructed. The sum of the leakage currents (protective conductor current) of the UPS and the connected devices exceeds 3.5 ma. Earth connection of the unit is essential before connecting supply.! CAUTION The supply to the load may be interrupted by opening all the switches or by turning the Maintenance Switch on the rear of the UPS to the Off position. DO NOT USE WATER to extinguish any fires that may occur in the area where the UPS is installed.! CAUTION Leakage currents Connect the protection earth (PE) safety conductor before connecting any other cables. Radio Interference The Liebert GXT T230 is a Radio Interference Class A Product. The UPS device may cause radio interference. Do not place it near devices that are particularly susceptible to electromagnetic interference (e.g., transmitters, receivers, radar, metal detectors and antitheft devices). NOTICE This is a product for commercial and industrial application in the second environment. Installation restrictions or additional measures may be needed to prevent disturbances. The product can meet the requirement of category C2 and may be used in residential, commercial and light industrial areas. Notes Regarding the EU Declaration of Conformity The Liebert GXT T230 conforms to the following European directives: 2006/95/EC - Directive of the council for adaptation of the legal regulations of the member states regarding electrical equipment for use within specific voltage limits. 2004/108/EC - Directive of the council for adaptation of the legal regulations of the member states regarding electromagnetic compatibility. Conformity is established through compliance with the following standards: EN EN EN EN Additional information regarding adherence to these directives is included in the appendices NSR and EMC of the EU Declaration of Conformity. If required, the EU Declaration of Conformity may be requested from Liebert. NOTICE TO EUROPEAN UNION CUSTOMERS: DISPOSAL OF OLD APPLIANCES This product has been supplied from an environmentally aware manufacturer that complies with the Waste Electrical and Electronic Equipment (WEEE) Directive 2002/96/CE. 3

10 The crossed-out wheelie bin symbol at right is placed on this product to encourage recycling wherever possible. Please be environmentally responsible and recycle this product through your recycling facility at its end of life. Do not dispose of this product as unsorted municipal waste. Follow local municipal waste ordinances for proper disposal provisions to reduce the environmental impact of waste electrical and electronic equipment (WEEE). For information regarding the scrapping of this equipment, go to Click on Products or Contacts and follow the links to obtain assistance. Information is also available by telephoning our worldwide technical support: Toll free: Toll number (in Italy):

11 Introduction and System Description 1.0 INTRODUCTION AND SYSTEM DESCRIPTION Congratulations on your purchase of the Liebert GXT T230. This system provides conditioned power to microcomputers and other sensitive electronic equipment. Upon generation, AC power is clean and stable. However, during transmission and distribution it is subject to voltage sags, spikes and complete power failure that may interrupt computer operations, cause data loss and damage equipment. The Liebert GXT T230 protects equipment from these disturbances. The Liebert GXT T230 is a compact, on-line UPS. An on-line UPS continuously conditions and regulates its output voltage whether utility power is present or not. It supplies connected equipment with clean sinewave power. Sensitive electronic equipment operates best from sinewave power. For ease of use, the Liebert GXT T230 features an LCD display for comprehensive user indications and programmable controls. It also provides self-diagnostic tests. The Liebert GXT T230 has an interface port for communication between the UPS and a network server or other computer system. This port provides detailed operating information including voltages, currents and alarm status to the host system when used in conjunction with Liebert s MultiLink software.! CAUTION This UPS may only be operated by qualified personnel. Figure 1 Liebert GXT T230 control panel 5

12 Introduction and System Description 1.1 Device Overview The Liebert GXT T230 is available at various nominal power ratings. The following table provides an overview of the various versions of the device: Table 1 Overview of UPS devices and batteries Type Model # Nominal power UPS with integrated battery Liebert GXT T VA/ 9000W Battery cabinet Liebert GXT3-240TBATTCE 240VDC Figure 2 Liebert GXT T230 front and rear views Parallel Port REPO Contacts Control Panel Control Keys Liquid Crystal Display Ventilation Louvers Liebert IntelliSlot port (covered) Maintenance Bypass Switch Bypass Source Input Circuit Breaker Input Breaker Parallel Port Cooling Fans Output Breaker External Battery Connector Block Hardwire Input and Output Connector Terminal Block 1.2 Options External Battery Cabinets Optional external battery cabinets are available to extend UPS autonomy in the event of mains interruption. The cabinets have the same dimensions, color scheme and design as the Liebert GXT T230. For technical data about external battery cabinets see Table 11 - UPS specifications. For connection notices see Table 2 - Connection data Optional Interfaces Refer to Communication for details. 6

13 Unpacking the UPS and Site Preparation 2.0 UNPACKING THE UPS AND SITE PREPARATION 2.1 Inspection Upon receiving your Liebert GXT T230, examine the packaging for any signs of mishandling or damage. While removing the packaging materials, inspect the UPS for damage. If any damage is noted, notify your local Liebert representative and carrier. Any damage or missing parts must be reported to the supplier within eight days of delivery. 2.2 Required Setup Equipment The following tools are required to set up your UPS: pallet jack utility knife or scissors star head screwdriver 2.3 Unpacking Take care when removing the packaging to avoid damaging the UPS. Do not dispose of the packing material. The original packaging material should be used if the UPS needs to be repackaged, such as for shipping. Check all packaging to ensure that no items are accidentally discarded. Remove the packaging in the sequence shown below. Figure 3 Unpacking Plywood Case Unlock Cushion Pallet Jack Cushions Ramp Cushion Ramp in Slot on Shipping Pallet 2.4 Storage If the UPS will not be installed immediately, store the unit indoors in a clean and dry area. Protect all the equipment, including its batteries, from extreme temperature, high humidity, spills and other damaging conditions. Refer to Table 12 for permissible environmental conditions for storage. 2.5 Handling The equipment must be kept upright at all times and handled with care. It may be damaged if dropped or subjected to severe impact. 7

14 2.6 Environmental Conditions Unpacking the UPS and Site Preparation The Liebert GXT T230 must be installed vertically, on a level and even surface and in an area protected from extreme temperatures, water, humidity and the presence of conductive powder or dust (see Table 12). Do not stack units; do not place any objects on top of a unit. 2.7 Access required The area must have sufficient space for installation procedures and for routine maintenance. Access doors must be sufficiently large to permit passage of the UPS. 2.8 Floor/Rack Loading Ensure that the floor where the UPS/batteries will be installed will support the unit s weight (see Table 11 for the unit s weight). 2.9 Inventory List The Liebert GXT T230 comes with: CD containing: Liebert MultiLink Shutdown Software Configuration Software User Manual USB cable Terminal block communication terminals Floor mount brackets Input power configuration jumpers Paralleling cable 2.10 Clearance The UPS is fitted with wheels for ease of movement over short distances. Leave 300mm (12in.) around the sides and rear of the unit to allow a flow of air and to provide access for any routine maintenance that may involve removal of the panels Repacking the UPS To repack the UPS, proceed as follows: 1. Do not pack the equipment until at least six hours have elapsed since the last recharge. 2. Make sure to re-use the original packing material to ship the UPS. 8

15 Installation 3.0 INSTALLATION 3.1 Electrical preparations Before you begin installation, the input source must be isolated and secured to prevent reconnection during installation. The input circuit breaker on the rear of the UPS must be in the Off position.! WARNING Installation may be carried out only by qualified technicians, conforming to applicable safety standards. Electric shock hazard: Even when the unit is disconnected from the mains, hazardous voltage may still be supplied by the battery. Both poles should be disconnected before carrying out maintenance work inside the UPS. For electrical installation, the nominal current rating of the source must be observed. The UPS is not suitable for connection to 16A subdistribution systems. 3.2 Current Table and Suggested Cable Sizes The following table indicates the currents and recommended sizes of the connecting cables in accordance with regulations IEC-287 and DIN VDE PVC-insulated copper cables 70 C) (158 F). 2. Air temperature surrounding the conduits should not be greater than 30 C (86 F). Table 2 NOTE Should there be any variation in the conditions, it will be necessary to verify whether the cable dimensions satisfy the requirements of IEC-287 and DIN VDE In cases where the cables are so long that they cause a drop in voltage of >3%, a larger size must be used. Connection data Description Unit UPS Power Rating kva 10-1/1 10-3/1 Connector size mm Max input current Arms Input cable size (and neutral) mm Max output current Arms Output cable size (and neutral) mm Earth cable size mm When the UPS is in Bypass mode, the entire output current of the UPS is passed through the phase L1 and Neutral cables. To simplify connection data, no distinction has been made between phase L1 and phases L2 and L3. The cable sizes are defined for the maximum current carried by the output cables.! WARNING Particularly sensitive equipment may be susceptible to interference. To prevent this, Liebert suggests: Mains input, output and external battery cables to the UPS in earthed, metal conduits, or use shielded cables Routing of cables (e.g. power supplies, communication or data lines) to other equipment, should be kept separate from that of UPS cables. 9

16 3.3 Neutral Connection Installation The installation of the UPS does not affect the existing neutral system. The neutral system may be affected if the UPS is operating with the neutral switched upstream. 3.4 External Protection and Isolating Devices External devices for the protection of cables and for isolating the UPS external to the UPS must be installed upstream of the equipment. Select and configure the isolating device according to Table 3. Such devices must be either curve C automatic circuit breakers or type GL/GG fuses. Disconnecting devices must be provided in building installations and other locations.! WARNING The following label must be displayed on all switching devices installed in the same electrical system as the UPS, even when they are located at a distance from the area. Table 3 ENSURE THAT THE UNINTERRUPTIBLE POWER SYSTEM IS ISOLATED BEFORE WORKING ON THIS CIRCUIT. External protection device data Protection Description Input Output Tower Power Rating (Phases In/Out) 10 - (1/1) 10 - (3/1) Fuse 120 Amps 40 Amps Breaker 96 Amps 32 Amps Fuse 90 Amps 90 Amps Breaker 63 Amps 63 Amps This table indicates the protection devices (circuit breakers and fuses) that must be installed for the protection of both the cables and the equipment. NOTE If an external battery cabinet is present it should be located next to the UPS unit. When such an option is supplied by Liebert it comes complete with protection devices and correctly-sized cables. When batteries are sourced from other suppliers, you should contact Customer Support Technical Service for correct sizing of protection devices and interconnection cables. 10

17 Installation 3.5 Installation of Differential Protection Devices To avoid spurious operation, differential protection devices must be: rated at differential current NOT LESS THAN 100mA a SELECTIVE type (delayed intervention) Type A Figure 4 Standard configuration - differential breaker D1 3.6 External Electrical Connections Remove the protective panel on the rear of the UPS to access the external electrical connections (see figure below). Once the cables have been connected they must be passed through the cable clamps that will hold them in position. Connect the earth cable first.! WARNING Ensure that the UPS is isolated before removing panels. Figure 5 Side view Protective panel over external connections NOTE Once installation has been completed, fix the UPS in position by screwing the stabilizing plates underneath the unit firmly to the floor. 11

18 3.7 Connecting Mains and Load Installation When connect the mains supply to the UPS refer to Figures 6 through 8. Choose the connection method according to the input supply characteristics. Connections must meet these requirements: The installer must provide circuit breaker protection according to local codes. The mains disconnect should be within sight of the UPS or have an appropriate lock-out. Maintain service space around the UPS or use flexible conduit. The installer must provide output distribution panels, circuit breaker protection, or emergency disconnect switches according to local codes. Output circuits must not share a common conduit with input circuits or any other wiring. The utility may be derived from a single-phase or three-phase source. Figure 6 Input and output connections with single source, single-phase input supply Mains 1 Input ~ Mains 2 Input ~ Output ~ Parallel Connection L1 L1 L2 L3 N GND BY N GND L N GND S1 S2 Factory-Supplied Jumper (W36) 230V 230V Input Figure 7 Input and output connections with dual source, single-phase input supplies Mains 1 Input ~ Mains 2 Input ~ Output ~ Parallel Connection L1 L1 L2 L3 N GND BY N GND L N GND S1 S2 Factory- Supplied Jumper (W35) 230V UPS Input 230V Bypass Input 230V Figure 8 Input and output connections with single source, three-phase input supply Mains 1 Input ~ Mains 2 Input ~ Output ~ Parallel Connection L1 L1 L2 L3 N GND BY N GND L N GND S1 S2 400V Input 230V Factory-Supplied Jumper (W34) 12

19 Installation Figure 9 Input and output connections with dual source, three-phase UPS, single-phase bypass input supplies Mains 1 Input ~ Mains 2 Input ~ Output ~ Parallel Connection L1 L1 L2 L3 N GND BY N GND L N GND S1 S2 400V Input 230V Bypass Input 230V NOTE During connection of a 3-phase input system, care must be taken to ensure each phase is connected to the corresponding phase on the input terminal block. Failure to make connections correctly could damage the unit. Output cable cannot exceed 10m (39ft). 3.8 Terminal Blocks for UPS The three-position maintenance switch includes the output breaker. Figure 10 Hardwire terminals 3.9 Connecting Power Cables 1. Open the UPS input breaker. 2. Open the UPS output breaker. 3. Remove the terminal area safety cover from the rear UPS panel. 4. Connect loads to the output terminals. Connect the mains to the corresponding input terminals (see Figure 3-5). If the reserve input is to be supplied separately, connect reserve line to the Mains 2 terminals. If the UPS is supplied by a common mains, connect the supplied jumper in the accessory kit marked W34 between the first L1 from the left (Mains 1) and BY (Mains 2) as shown in Figure 8. 13

20 3.10 External Tower Batteries Installation One or more battery cabinets may be connected to the Liebert GXT T230. A cable to connect the battery cabinet and the Liebert GXT T230 is supplied with each battery cabinet. Plug this cable into the battery cabinet and UPS battery sockets slotted fittings on each and ensure that the connection is properly made. Since your UPS has integrated batteries, a compensating current may occur during connection. Figure 11 Liebert GXT T230 with External Battery Cabinet 3.11 Connecting an External Battery Extension NOTE External battery extensions can be replaced during normal operation of the UPS (hot swappable). However, the batteries must NOT be changed when the UPS is in the status Battery Mode operation. The unit checks the battery voltage (a beep is heard) once more and stays in bypass till a constant battery voltage is present.! CAUTION Battery maintenance must be carried out by authorized personnel observing the necessary precautions. 14

21 Installation 3.12 Battery Precautions The batteries installed in the UPS and within the battery extensions may contain electrolyte. Under normal conditions, the containers are dry. A damaged battery may leak electrolyte, which can cause skin and eye irritation. Should this happen, wash the affected area with plenty of water and seek immediate medical attention. Do not open or damage batteries. The released electrolyte is toxic. Voltage is always present on the battery contacts. Even when discharged, a battery has the capacity a high short circuit current which, in addition to causing damage to the battery itself and associated cables, may expose the operator to the risk of burns. The following precautions should be observed when working with batteries: Remove watches, rings and other metal objects. Use tools with insulated handles. The voltage of a single cell of a battery is not dangerous. However a number of cells or battery blocks, connected in series, can produce hazardous voltages. The battery cabinet must not be kept in storage or not used for periods exceeding six months (at 20 C [68 F]) without being recharged (having been charged to 100% at the beginning of any such period). If this period is exceeded, it is essential that the batteries be recharged (which does not require the UPS to be switched on; the UPS just needs to be connected to the mains). If these conditions are not met, the battery performance can no longer be guaranteed. We recommend recharging the batteries at least once every four months. Since new batteries often do not provide full capacity after the initial charge, it may be necessary to carry out a number of discharge/recharge cycles before optimum performance is reached. When replacing batteries, replace with the same type and number of batteries and battery packs. In order to protect the environment, batteries must be disposed of in accordance with local laws concerning the safe disposal of toxic and harmful waste. Do no not dispose of batteries in a fire. The batteries may explode Configuration Program The final step of installation may require custom configuration of your UPS using the enclosed configuration program. Some configuration settings may be changed only while the UPS is Off. These should be set before the UPS is put into full-time use. For most users operating with 230VAC, the factory default settings will be adequate Liebert GXT T230 Configuration Program Features Select one of the three L-N output voltages to match local voltage. Enable/disable auto-restart. Select frequency converter operation with a fixed output frequency of 50 or 60 Hz. Set the Low battery warning alarm time from 2 to 30 minutes. Enable/disable auto-battery test. Set auto-battery test frequency to 7, 14, 21 or 28 days. Specify the number of external battery cabinets connected to the UPS to adjust the remaining run time calculations reported by the system software What You Will Need In addition to the Liebert GXT T230, you will need the configuration program CD and USB cable included in the UPS accessory pack. You must be running Microsoft Windows XP or later on your computer. 15

22 Operation 4.0 OPERATION 4.1 Normal Operating Block diagram The Liebert GXT T230 consists of several main components: 2 mains supplies (mains and reserve) Rectifier/booster, inverter and charger Internal electronic bypass 2 input breakers Maintenance bypass breaker TVSS filter Integrated battery (expandable) Figure 12 Overview of UPS tower Maintenance Bypass Switch Maintenance Bypass Mains1 Mains2 (Reserve) N By N L 1 L 2 L 3 L2,L3 at 10kVA device only Electronic Bypass Rectifier/ Booster Inverter L N S 2 S 1 L N Load External Battery 10kVA Tower 16

23 Operation 4.2 Control Panel The display text is shown as a 10kVA UPS. Figure 13 Control panel Fault Indicator Battery Indicator UPS Output On Indicator Bypass Indicator LCD Enter key Escape key Menu Up key Menu Down key Controls and Messages Table 4 Lighted LEDs LED Indicator LED Color Description UPS ON Green UPS is online and operating normally BYPASS Amber Load is supplied by the mains via automatic bypass BATTERY Amber Load is supplied by the battery FAULT Red An error has occurred within the UPS Flashing LED When the BYPASS LED is flashing, the mains is out of tolerance! CAUTION Do not switch Off the UPS or switch from online to bypass while in this status, otherwise load will no longer be supported. The following displays the menu structure that can be accessed through the control panel. Press the Menu Up or Menu Down buttons to scroll through each menu. Press Enter to choose an entry. 17

24 Operation Figure 14 System block, menu structure UPS ON/OFF Alarm Ctrl Control Menu Batt Test Batt Test Abort Test Status Menu Contrast Test Report Start Window Parallel Menu Output Volt Audible Alarm Batt Pack System Status Main Menu Test Intvl Setup Menu DC Start UPS ID No. No. of Unit Tag Number Language Event Log Log Menu Clear Log Types About Menu IP Version 18

25 Operation Table 5 Displayed text system block and main menu Item# and Name Description START WINDOW UPS 10kVA Self Testing Control Status Parallel MAIN MENU Setup Log About UPS ON/OFF Turn On Shut Down Turn Off To Bypass CONTROL MENU Alarm Ctrl Batt Test Alarm On Alarm Off Batt Test Abort Test Test Report STATUS MENU PARALLEL MENU Contrast Measure Value Unit Output Volt V Output Freq 0.1Hz Output Curr A Output Watt W Output VA VA Load Level % Input Volt V L2 Input Volt V L3 Input Volt V Input Freq 0.1Hz Batt Volt V Batt Cap % Backup Time Min,sec Elapsed Time day:hr:min;sec Tag Number SysOutI A SysOutV V SysOutF Hz SysOutW W SysOutVA VA SysLoadPer % Darker Lighter 19

26 Operation Table 5 Displayed text system block and main menu Item# and Name Description SETUP MENU Setting item Setting(level 1) Audible Alarm Disable/Enable Output Volt 220V/230V/240V Batt Pack 1-4 Test intvl DC Start Disable/Enable UPS ID No. 1-3 No. of Unit 1-3 Tag Number LOGGING MENU FIRMWARE VERSION Language Event log Clear log * Max 4 fault event record English/French/Spanish/ German/Italian/Russian Types Liebert Corporation GXT 10KVA Liebert GXT3 10kVA IP Web: Version Display Firmware version MCU Version:V*** DSP Version: V*** Warning Indicators If a warning indicator appears, the UPS continues to operate. The warning message alternates with UPS mode once a second (see Table 6) The warning indicators are described below: Table 6 Warning indicators Warning Cause Corrective Steps 1 No Redundancy 2 InvASynFault 3 ParaCommuErr 4 CurShareFault 5 ParaFreqErr 6 Byp Reminder 7 L2 or L# Fail Check L2, L3 input fuse 8 UtilFail N/A 9 BattUnderVolt N/A 20

27 Operation Fault Indicators If a fault occurs, the UPS automatically switches to BYPASS mode. Only in the case of a battery disconnection fault will the original operating mode be maintained. The fault message alternates with UPS mode once a second, the red fault LED on the control panel lights up and the alarm sounds continuously. If a fault occurs, proceed as follows: Alarm operation The alarm can be switched On or Off. Clear Fault Present fault condition can be reset if fault condition is cleared, either automatically or by the user. Fault information A maximum of four faults can be displayed in this window. All fault displays include: The nature of the event The time of the event The fault indicators are: Table 7 Display faults Fault Cause Corrective Steps 1 Comm Shutdown Call customer service 2 Inv Fault Call customer service 3 Over Temp Reduce load 4 Batt Test Fail Call customer service 5 PFC Failure Call customer service 6 Over load Reduce load 7 DCDC Failure Call customer service 8 DC BUS Fault Call customer service 9 Charger Fault Call customer service 10 REPO N/A 11 Byp Feedback Call customer service 12 Startup No Batt Check battery 13 Mnt Byo Swt On Call customer service 14 Fan Fault Call customer service 15 Batt Disconnect Check battery connector 16 ParaCableFault Call customer service 17 ParaAddOverlap Call customer service 18 Turn On Fail Call customer service 4.3 Startup Preparations Before switching On the UPS and supplying the load, ensure the following: The ventilation grilles are unobstructed The earth connection is in place The consumer breakers are in the Off (0) position The UPS rear panel breakers are in the Off (0) position! WARNING As soon as the UPS is connected to input power, the output sockets are live, even if the UPS is not yet switched On. Once recharging has been completed, the UPS is ready for use.! WARNING Do not connect any devices that may overload the UPS or draw DC current. NOTE You may experience problems with the electrical supply if you do not follow these instructions. 21

28 Operation 4.4 UPS Startup Procedure - Single Block 1. Ensure all switches and circuit breakers upstream of the UPS are closed. 2. Ensure mains connections are secured at the UPS input. UPS requires twin supplies or one supply and one bridge. If the UPS is supplied from one mains only, mains connectors have to be fixed to the terminals section Mains 1. The jumper must be fixed as: From L1 - mains 1 to BY - mains 2 3. Switch both Input breakers (mains 1 and mains 2/reserve) to ON (I). The LCD displays Self testing, Please wait (see Controls and Messages). 4. Press OK and scroll to find the Setup menu. 5. Check and adjust if necessary parameters for language, voltage and battery pack(s) (see Table 5 for more information). The default language is English. 6. Close any external switches connecting the load (if present). 7. Press the Menu button, select Control and press OK. 8. Select Turn UPS ON/OFF and press OK. The LCD will display Turn ON. 9. Press OK to switch On the inverter. The LCD will display Powering UP.! WARNING If the load indication is greater than 100%, then the energy demand from the connected load exceeds the power rating of the UPS. In addition to a warning being displayed on the front panel, a beep (once a second) will sound. 4.5 UPS Shutdown Procedure All Ratings NOTE Carrying out this procedure will interrupt the supply to load. 1. Press the Menu button, select Control and press OK. 2. Select UPS ON/OFF and press OK. The LCD displays To Bypass. 3. Press OK to switch Off the inverter. 4. Open any external switches connecting the load (if present). 5. Switch both input switches to the Off Position. 6. Ensure all switches and circuit breakers upstream of the UPS are open. 7. Ensure that all LEDs on the control panel are Off. The UPS is now shut down. 4.6 Maintenance Bypass Procedure 1. Press the Menu button, select Control and press OK. 2. Select UPS ON/OFF and press OK. The LCD displays To BYPASS. 3. Press OK to switch Off the inverter and transfer to internal bypass. 4. Remove the safety cover from the Maintenance switch, and turn On the Maintenance Bypass Breaker. NOTE At this point, the load is no longer protected against interruptions and disturbances of the mains. 5. Switch output and input switches to the Off position. 6. The UPS is now switched Off, all LEDs are Off and the load is supplied directly from the mains. 22

29 Operation 4.7 Return from Maintenance Bypass Procedure 1. Ensure all switches and circuit breakers upstream of the UPS are closed. 2. Switch both input switches to the On position. 3. Wait at least 30 seconds until the output voltage has stabilized (the yellow LED is lit). 4. Switch the Maintenance switch from BYPASS to UPS and replace the cover. The load is now supplied via internal bypass. 5. Press the Menu button, select Control and press OK. 6. Select UPS ON/OFF and press OK. The LCD displays UPS to ON. 7. Press OK to switch On the inverter. 4.8 Functional Test NOTE Supply to the load is not guaranteed during this test. The test should not be carried out if a critical load is connected to the UPS. The Liebert GXT T230 s controls permit testing the UPS to ensure that the load will be supplied in the event of a mains failure. Before beginning, ensure that the batteries are fully charged. Simulate a mains failure by interrupting the mains supply to the UPS. You can do this by switching Off the input power circuit breaker on the rear panel of the UPS. If the mains supply to the Liebert GXT T230 is protected by an external circuit breaker, opening that circuit breaker will interrupt the mains supply and simulate a power failure. The Liebert GXT T230 is operating properly and the batteries are charged if: An audible signal is heard at four-second intervals The UPS On LED indicator turns Off When the interval between the audible signals decreases to 10 seconds, the UPS has battery reserve energy to supply the load for a maximum of two more minutes. After two minutes, the Liebert GXT T230 will automatically shut down. If the batteries do not supply the load during the simulation, refer to Troubleshooting. To end the simulated mains failure, restore the input power supply to the UPS. The UPS is now ready for operation. NOTE The batteries must be recharged before the complete emergency supply period is again available. 4.9 Remote Emergency Power Off The UPS is equipped with an Emergency Power Off circuit. A factory-installed jumper allows the UPS to operate without an external shutoff switch. If a Remote Emergency Power Off switch is required, a switch with normally closed contacts must be used. Connect the switch contacts to the UPS by removing the factory-installed jumper as shown in Figure

30 Operation Figure 15 REPO connections 4.10 Self-Tests Lamp Test 1. With the Liebert GXT T230 connected to the mains, press the Menu button, select Control and press OK. Select UPS ON/OFF and press OK. The LCD will show To BYPASS. 2. Press OK to switch the inverter to Bypass mode. A system confirmation beep will sound Battery Test NOTE This test involves putting the Liebert GXT T230 into bypass mode. The load is not protected against any mains disturbance or interruptions while the UPS is in bypass mode. NOTE During the test a beep will sound as though the device is operating in battery mode. 1. Press the Menu button. 2. Select Control and press OK. 3. Select BATT TEST and press OK. A system confirmation beep will sound and the load will be supplied by the battery. If the test is successful, the BATT LED will turn off, and the UPS will return to Line mode. If the UPS circuitry detects a battery malfunction, the system will display an alarm (see Controls and Messages) See Table 8 for battery test report messages: Table 8 Menu entry Battery test report Battery test report messages Display In Progress Test OK! Test fail 24

31 Maintenance 5.0 MAINTENANCE 5.1 Testing, Replacing and Disposing of Batteries The Liebert GXT3 is designed to allow the user to replace the internal battery pack safely. Users should use the internal battery pack part numbers in Table 9 for Liebert GXT3 UPS and External Battery Cabinets. Refer to for internal battery pack part numbers for Liebert GXT3 UPS and Liebert External Battery Cabinets: Table 9 Replacement battery pack Unit Model Number Replacement Internal Battery Pack Model Number Quantity Required Liebert UPS: GXT T230 GXT3-240RTBKIT 2 Liebert External Battery Cabinet: GXT3-240TBATTCE GXT3-240RTBKIT 2 Read all safety cautions before proceeding. Contact your local dealer or Emerson representative to obtain the part number and pricing of the appropriate replacement battery pack. Disposal of the UPS and batteries should be carried out by a certified disposal company. Observe all local regulations and laws. Exhausted accumulator batteries are classified as harmful toxic waste and, as such, the law demands that they be disposed of by an authorized recycling centre. The typical battery life cycle is three to five years, at an ambient temperature of 77 F (25 C), but is also dependent on the frequency and duration of mains failures. The battery test (see Battery Test) should be run periodically (every 6 to 12 months) to ascertain the general condition of the batteries and to ensure maximum run time. 25

32 5.2 Easy Battery Replacement Maintenance Open the front panel as shown below. Ensure that a certified service engineer is present to replace the batteries. 1. Open the battery tray DC connectors as shown. 2. Remove the battery trays from the cabinet. 3. Replace the old batteries with a new set. Replacement batteries must be the same type installed at the factory. 4. Reconnect the battery cables. Figure 16 Removing front panel and unlocking battery trays Figure 17 Disconnecting battery tray and battery packs DC connectors 26

33 5.3 Storage Maintenance For extended storage at ambient temperatures cooler that 25 C (77 F), the batteries should be charged for five hours once every four months. At higher storage temperatures. Emerson recommends charging batteries for five hours every two months. After five hours, disconnect from the mains supply or switch Off the input miniature circuit breaker of the UPS. Then remove the UPS connections in the opposite sequence to that described in Installation. Record the battery charging date in the vicinity of the UPS, for example, on its packaging. 5.4 Cleaning 1. Do not clean the UPS with scouring powder or solutions that may dissolve plastic. 2. Do not allow liquid to get inside the UPS. 3. Make sure that the air vents on the UPS are not obstructed. Remove dust from the air vents with a vacuum cleaner. 4. Clean the outside of the UPS by wiping the housing with a dry or slightly damp cloth. 27

34 Communication 6.0 COMMUNICATION 6.1 Communication Interface Port The Liebert GXT3 UPS has a terminal block on the rear of the UPS unit. Several signals are provided on this port and are assigned as follows. 6.2 Terminal Block The terminal block includes eight pins in four sets, as shown in Figure 18. Figure 18 Terminal block pin layout Low Battery Warning On-Battery Warning Any Mode Shutdown Battery Mode Shutdown Any Mode Shutdown The purpose of Any Mode Shutdown is to shut down the UPS output by turning Off the rectifier, inverter and static switch so that there is no power to the loads. Any Mode Shutdown can be operated locally or remotely: Local Any Mode Shutdown can be performed by shorting the pins in Set 3. Remote Any Mode Shutdown can be performed using a switch connected to the pins in Set 3 and mounted at a remote location. Activation of the Any Mode Shutdown will be logged as an event in the event history log. NOTE Remote Power Off will be performed either by NO or NC contact of Any Mode Shutdown. The current limited source (+12VDC, 50mA) will be available from UPS. The connection to UPS for remote connection will be via terminal block connector. Any Mode Shutdown wiring must conform to all national, regional and local wiring codes and laws.! WARNING When the Auto-enable output option is selected and the UPS output is disabled using the pins in Set 3, the Liebert GXT3 s output can turn On automatically and without warning if the connection to the pins in Set 3 is changed. 28

35 6.2.2 Battery Mode Shutdown Communication Battery Mode Shutdown permits shutting down the UPS by turning Off the rectifier, inverter and static switch so that there is no power to the load when the UPS is On Battery. The auxiliary power for the UPS will still be active. Battery Mode Shutdown can be performed locally or remotely: Local Battery Mode shutdown can be performed by shorting the pins in Set 4. Remote Battery Mode Shutdown can be performed using a switch connected to the pins in Set 4 and mounted at remote location. Activation of the Battery Mode Shutdown will be logged as an event in the event history log On Battery NOTE Remote Power Off will be performed by NO contact. The current limited source (+12VDC, 50mA) will be available from UPS. The connection to the Liebert GXT3 for remote connection will be via terminal block connector. Battery Mode Shutdown wiring must conform to all national, regional and local wiring codes and laws. This signal must last for 1.5 seconds or longer. A battery shutdown signal will not cause an immediate shutdown. It will start a 2-minute shutdown timer. This timer cannot be stopped once triggered. If the utility power returns during this countdown, the Liebert GXT3 will still shut down and must remain shut down for 10 seconds. Whether the UPS turns back On when the power is restored depends on the auto-restart setting. On Battery signal is a Normally Open (NO) dry contact. When the UPS is supplying output power from the battery this dry contact will be closed Low Battery Low Battery signal is a Normally Open (NO) dry contact. When the UPS is supplying output power from the battery and has reached the Low Battery Warning time selected in the configuration program, this dry contact will be closed. NOTE The rated values for the dry contacts are: Rated Voltage: 30V (AC or DC) Rated Current: 300mA 6.3 Liebert IntelliSlot Communication Cards The Liebert IntelliSlot port accepts three optional cards: Liebert IntelliSlot SNMP Card Liebert IntelliSlot Relay Card Liebert IntelliSlot 485 Card. The Liebert IntelliSlot SNMP Card provides SNMP monitoring and control of the UPS across the network. The Liebert IntelliSlot Relay Card provides dry contact relay outputs for custom-wired applications and delivers support for built-in shutdown for AS/400 systems. The Liebert IntelliSlot 485 Card is used to connect the UPS and a BMS. Follow instructions provided with the Liebert IntelliSlot card to configure Liebert MultiLink, the UPS or any additional ancillary product for the Liebert GXT3. These instructions are available at multilink.liebert.com 29

Extended Battery Cabinet for Nfinity

Extended Battery Cabinet for Nfinity POWER PROTECTION Extended Battery Cabinet for Nfinity USER MANUAL TABLE OF CONTENTS IMPORTANT SAFETY INSTRUCTIONS................................... 1 ELECTROMAGNETIC COMPATIBILITY.......................................

More information

Liebert GXT3 UPS 230V 700VA-3000VA

Liebert GXT3 UPS 230V 700VA-3000VA AC Power For Business-Critical Continuity Liebert GXT3 UPS 230V 700VA-3000VA User Manual TABLE OF CONTENTS IMPORTANT SAFETY PRECAUTIONS................................................1 SAVE THESE INSTRUCTIONS.....................................................1

More information

Users Manual. Defender 1 8.0KW to 14.0KW Online Emergency Lighting Inverter. Technical Manual # Revision B

Users Manual. Defender 1 8.0KW to 14.0KW Online Emergency Lighting Inverter. Technical Manual # Revision B Users Manual Defender 1 8.0KW to 14.0KW Online Lighting Inverter Technical Manual #018-0102-01 Revision B Phone: 1.877.DSPM.POWER 1.877.377.6769 Fax: 909.930.3335 Website: www.dspmanufacturing.com E-Mail:

More information

Liebert GXT4. User Manual 700VA ~ 3000VA (230V)

Liebert GXT4. User Manual 700VA ~ 3000VA (230V) Liebert GXT4 User Manual 700VA ~ 3000VA (230V) Important Safety Precautions Warning Observe all cautions and warnings in this manual. Failure to do so may result in serious injury or death. Refer all

More information

Users Manual. Cobra Plus Stand-By Emergency Lighting Inverter. Technical Manual # Revision B

Users Manual. Cobra Plus Stand-By Emergency Lighting Inverter. Technical Manual # Revision B Users Manual Cobra Plus Stand-By Lighting Inverter Technical Manual #018-0110-01 Revision B Phone: 1.877.DSPM.POWER 1.877.377.6769 Fax: 909.930.3335 Website: www.dspmanufacturing.com E-Mail: techsupport@dspmanufacturing.com

More information

TOWER MAXI T SINGLE CONVERSION ON LINE UPS SYSTEMS

TOWER MAXI T SINGLE CONVERSION ON LINE UPS SYSTEMS INSTRUCTION MANUAL TOWER MAXI T SINGLE CONVERSION ON LINE UPS SYSTEMS September 2000 TOWER UPS DISTRIBUTION (PTY) LTD 1 1. INTRODUCTION T A B L E O F C O N T E N T S 1.1 General Description... 3 1.2 Features...

More information

IMPORTANT SAFETY INSTRUCTIONS

IMPORTANT SAFETY INSTRUCTIONS Chloride Linear Plus Rack-Mount UPS User Instruction Manual IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS. This manual contains important instructions for models: LP061XHR LP101XHR LPBP100-2 Follow

More information

Installation Guide Smart-UPS On-Line SRT1000/SRT1500 XLA Tower/Rack-Mount

Installation Guide Smart-UPS On-Line SRT1000/SRT1500 XLA Tower/Rack-Mount Installation Guide Smart-UPS On-Line SRT1000/SRT1500 XLA Tower/Rack-Mount Important Safety Messages Read the instructions carefully to become familiar with the equipment before attempting to install, operate,

More information

User Manual V1.1 OptiFlex 1100 / OptiFlex 2000

User Manual V1.1 OptiFlex 1100 / OptiFlex 2000 User Manual V1.1 OptiFlex 1100 / OptiFlex 2000 Uninterruptible Power Supply System Table of Contents 1. Important Safety Warning 2 1-1. Transportation 2 1-2. Preparation 2 1-3. Installation 2 1-4. Operation

More information

On Line UPS. LUC 1000E / LUC 2000E / LUC 3000E User Manual

On Line UPS. LUC 1000E / LUC 2000E / LUC 3000E User Manual On Line UPS LUC 1000E / LUC 2000E / LUC 3000E User Manual Save This Manual Please read this manual carefully prior to storage, installation, wiring, operation and maintenance of the UPS. This manual contains

More information

Liebert GXT & 6000VA RT230 Rack-Tower models GUIDE SPECIFICATIONS 1.0 GENERAL

Liebert GXT & 6000VA RT230 Rack-Tower models GUIDE SPECIFICATIONS 1.0 GENERAL GXT4 5000 & 6000VA RT230 Rack-Tower models GUIDE SPECIFICATIONS 1.0 GENERAL 1.1 SUMMARY This specification shall define the electrical and mechanical characteristics and requirements for a continuousduty,

More information

Installation Guide Smart-UPS On-Line SRT1000/1500 UXI-NCLI, SRT1000/1500 UXI-LI, Tower/Rack-Mount

Installation Guide Smart-UPS On-Line SRT1000/1500 UXI-NCLI, SRT1000/1500 UXI-LI, Tower/Rack-Mount Installation Guide Smart-UPS On-Line SRT1000/1500 UXI-NCLI, SRT1000/1500 UXI-LI, Tower/Rack-Mount Important Safety Messages Read the instructions carefully to become familiar with the equipment before

More information

User Manual Digital Energy Uninterruptible Power Supply ML Series UPS VA GE Digital Energy Power Quality

User Manual Digital Energy Uninterruptible Power Supply ML Series UPS VA GE Digital Energy Power Quality GE Digital Energy Power Quality User Manual Digital Energy Uninterruptible Power Supply ML Series UPS 350-500-700-1000 VA GE imagination at work GB User Manual Digital Energy Uninterruptible Power Supply

More information

USER S MANUAL CONTENTS. Uninterruptible Power Supply 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION... 4

USER S MANUAL CONTENTS. Uninterruptible Power Supply 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION... 4 USER S MANUAL ON-LINE 1K/2K/3KVA CONTENTS 1. INTRODUCTION...... 1 2. SAFTY INSTRUCTION.......... 2 3. CABLE CONNECTION.......... 4 4. SYSTEM DESCRIPTION............ 5 5. UPS OPERATION...... 12 6. TROUBLE

More information

Liebert GXT3 230V, ,000VA

Liebert GXT3 230V, ,000VA AC Power For Business-Critical Continuity Liebert GXT3 230V, 5000-10,000VA User Manual TABLE OF CONTENTS IMPORTANT SAFETY INSTRUCTIONS................................................1 SAVE THESE INSTRUCTIONS.................................................1

More information

User Manual Rittal PMC UPS 6kVA

User Manual Rittal PMC UPS 6kVA User Manual Rittal PMC UPS 6kVA Germany Rittal GmbH & Co. KG Auf dem Stützelberg D-35745 Herborn Tel.: ++49-27 72-5 05-0 Fax: ++49-27 72-5 05-23 19 Internet: www.rittal.de 26 Contents 1. Introduction...

More information

User Manual. Digital Energy Uninterruptible Power Supply ML Series UPS VA. GE Digital Energy Power Quality. GE imagination at work

User Manual. Digital Energy Uninterruptible Power Supply ML Series UPS VA. GE Digital Energy Power Quality. GE imagination at work GE Digital Energy Power Quality User Manual Digital Energy Uninterruptible Power Supply ML Series UPS 350-500-700-1000 VA GE Consumer & Industrial SA General Electric Company CH 6595 Riazzino (Locarno)

More information

User Manual Solar Charge Controller 3KW

User Manual Solar Charge Controller 3KW User Manual Solar Charge Controller 3KW Version: 1.3 CONTENTS 1 ABOUT THIS MANUAL... 1 1.1 Purpose... 1 1.2 Scope... 1 1.3 SAFETY INSTRUCTIONS... 1 2 INTRODUCTION... 2 2.1 Features... 2 2.2 Product Overview...

More information

Match 19" GE Digital Energy. Uninterruptible Power Supply VA. Technology for the Digital World. Match 19" UPS.

Match 19 GE Digital Energy. Uninterruptible Power Supply VA. Technology for the Digital World. Match 19 UPS. Match 19" Uninterruptible Power Supply 700-1500 VA Manufactured by: General Electric Company Telephone +41 (0)91 / 850 51 51 CH 6595 Riazzino (Locarno) Fax +41 (0)91 / 850 51 44 Switzerland Website www.gedigitalenergy.com

More information

USER MANUAL MPS 1-5KW SERIES

USER MANUAL MPS 1-5KW SERIES USER MANUAL MPS 1-5KW SERIES Low Series Frequency Solar and Wind Power Charging Inverter CONTENTS 1 WWW.NEXTGENNRG.COM 1. Introduction... 3 2. Profile Structure 4 2.1. Working Principle 4 2.2.Product Features..5

More information

1. INTRODUCTION SYSTEM DESCRIPTION Front Panel CONNECTION AND OPERATION TROUBLESHOOTING...8

1. INTRODUCTION SYSTEM DESCRIPTION Front Panel CONNECTION AND OPERATION TROUBLESHOOTING...8 Contents : 1. INTRODUCTION...1 2. IMPORTANT SAFETY INSTRUCTIONS...2 3. SYSTEM DESCRIPTION...4 3.1 Front Panel...4 4. CONNECTION AND OPERATION...6 5. TROUBLESHOOTING...8 6. MAINTENANCE...9 6.1 Operation...9

More information

User Manual. NetGuard IMPORTANT. PSD 650/1200/1600 Line Interactive UPS Uninterruptible Power Supply System. UPS Monitoring Software

User Manual. NetGuard IMPORTANT. PSD 650/1200/1600 Line Interactive UPS Uninterruptible Power Supply System. UPS Monitoring Software User Manual Thank you for purchasing the Defender 650/1200/1600. It is designed to provide safe and reliable power protection to your precious electronics equipment. Before you start using the product,

More information

Switching DC Power Supply

Switching DC Power Supply 99 Washington Street Melrose, MA 02176 Phone 781-665-1400 Toll Free 1-800-517-8431 Visit us at www.testequipmentdepot.com Model 1693, 1694 Switching DC Power Supply INSTRUCTION MANUAL 1 Safety Summary

More information

Liebert GXT MT+ User Manual VA Installer/User Guide

Liebert GXT MT+ User Manual VA Installer/User Guide Liebert GXT MT+ User Manual - 1000-3000 VA Installer/User Guide Table of Contents 1. Important Safety Warning 1 1-1. Transportation 1 1-2. Preparation 1 1-3. Installation 1 1-4. Operation 1 1-5. Maintenance,

More information

BRAVER UPS. (Uninterruptible Power System) User s Manual

BRAVER UPS. (Uninterruptible Power System) User s Manual BRAVER UPS (Uninterruptible Power System) User s Manual Safety CAUTION! This UPS utilizes voltages that may be hazardous. Do not attempt to disassemble the unit. The unit contains no user replaceable parts.

More information

Thank you for choosing EATON products. Safety information and operating instructions are included in this manual. Do not attempt to operate the UPS

Thank you for choosing EATON products. Safety information and operating instructions are included in this manual. Do not attempt to operate the UPS Thank you for choosing EATON products. Safety information and operating instructions are included in this manual. Do not attempt to operate the UPS until reading through this manual carefully. Observe

More information

Installation and user manual. 5SC 500i 5SC 750i 5SC 1000i 5SC 1500i ENGLISH. Copyright 2013 EATON All rights reserved.

Installation and user manual. 5SC 500i 5SC 750i 5SC 1000i 5SC 1500i ENGLISH. Copyright 2013 EATON All rights reserved. ENGLISH Installation and user manual 5SC 500i 5SC 750i 5SC 1000i 5SC 1500i Copyright 2013 EATON All rights reserved. Service and support: Call your local service representative Certification Standards

More information

ULTIMA W SERIES. 1K/2K/3K Online UPS USER MANUAL

ULTIMA W SERIES. 1K/2K/3K Online UPS USER MANUAL ULTIMA W SERIES 1K/2K/3K Online UPS USER MANUAL Maruson Technology Corporation 18557 East Gale Avenue City of Industry, California 91748, U.S.A. Tel: +1-626-912-8388 Fax: +1-626-912-8680 Toll Free: 1-888-MARUSON

More information

Whad 0.8, 1, 1.5 kva. Manuel d installation Installation manual. Part. LE05733AA-07/12-01 GF

Whad 0.8, 1, 1.5 kva. Manuel d installation Installation manual. Part. LE05733AA-07/12-01 GF Manuel d installation Installation manual Part. LE05733AA-07/12-01 GF Index 1 Introduction 18 2 Conditions for use 19 3 Installation 20 4 Visual and acoustic warning signals 22 5 ups diagnostic software

More information

User Manual. PF0.9 1K/2K/3K Online UPS. Uninterruptible Power Supply System. Version: 1.3

User Manual. PF0.9 1K/2K/3K Online UPS. Uninterruptible Power Supply System. Version: 1.3 User Manual PF0.9 1K/2K/3K Online UPS Uninterruptible Power Supply System Version: 1.3 Table of Contents 1. Important Safety Warning... 1 1-1. Transportation... 1 1-2. Preparation... 1 1-3. Installation...

More information

USER MANUAL. Power GUARD UPS. Uninterruptible Power System

USER MANUAL. Power GUARD UPS. Uninterruptible Power System USER MANUAL Power GUARD UPS Uninterruptible Power System IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS This manual contains important instructions for Power GUARD that should be followed during

More information

Liebert GXT VA RT230 Rack-Tower model GUIDE SPECIFICATIONS 1.0 GENERAL

Liebert GXT VA RT230 Rack-Tower model GUIDE SPECIFICATIONS 1.0 GENERAL 1.1 SUMMARY Liebert GXT3 10000VA RT230 Rack-Tower model GUIDE SPECIFICATIONS 1.0 GENERAL This specification shall define the electrical and mechanical characteristics and requirements for a continuousduty,

More information

SOS SERIES SOS1 SOS2. Spares On Site Battery Cabinet Installation Guide rEV3

SOS SERIES SOS1 SOS2. Spares On Site Battery Cabinet Installation Guide rEV3 Atlantic Battery Systems 1065 Market Street Paterson, NJ 07513 Phone: (800) 875-0073 Fax: (973) 523-2344 sales@atbatsys.com www.atbatsys.com SOS1 SOS2 SOS SERIES Spares On Site Battery Cabinet Installation

More information

USER S MANUAL CONTENTS. Uninterruptible Power Supply 1. INTRODUCTION SAFTY INSTRUCTION SYSTEM DESCRIPTION... 4

USER S MANUAL CONTENTS. Uninterruptible Power Supply 1. INTRODUCTION SAFTY INSTRUCTION SYSTEM DESCRIPTION... 4 USER S MANUAL PowerWalker VFI 1000 / 3000VA CONTENTS 1. INTRODUCTION...... 1 2. SAFTY INSTRUCTION......... 2 3. SYSTEM DESCRIPTION......... 4 4. CABLE CONNECTION......... 7 5. OPERATION...... 8 6. TROUBLE

More information

Pulsar EXtreme CLA 1500C

Pulsar EXtreme CLA 1500C www.mgeups.com MGE UPS SYSTEMS Pulsar EXtreme CLA 500C Installation and user manual 503998EN/AA - Page Introduction Thank you for selecting an MGE UPS SYSTEMS product to protect your electrical equipment.

More information

TECHNICAL DATA SHEET KVA UPS Systemss

TECHNICAL DATA SHEET KVA UPS Systemss Återförsäljare: Tre Röda AB TillingeHagby 7-745 94 ENKÖPING Tel: 08-560 200 22 e-post: info@treroda.nu http: www.treroda.nu When the INSIDE is important make the OUTSIDE Cannon TECHNICAL DATA SHEET 400-500-600-800

More information

1. Important Safety Warning

1. Important Safety Warning Table of Contents 1. Important Safety Warning... 1 1-1. Transportation... 1 1-2. Preparation... 1 1-3. Installation... 1 1-4. Operation... 1 1-5. Maintenance, service and faults... 2 2. Installation and

More information

Pulsar Evolution 2200/3000/3000 XL

Pulsar Evolution 2200/3000/3000 XL www.mgeups.com Pulsar Evolution 2200/3000/3000 XL Installation and user manual MGE UPS Systems 1660 Scenic Avenue Costa Mesa, CA 92626 (714) 557-1636 For service call 1-800-438-7373 www.mgeups.com IMPORTANT

More information

Liebert PSA VA. Installer/User Guide

Liebert PSA VA. Installer/User Guide Liebert PSA4 1000 1500 VA Installer/User Guide Technical Support Site If you encounter any installation or operational issues with your product, check the pertinent section of this manual to see if the

More information

Liebert GXT & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL

Liebert GXT & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL 1.1 SUMMARY Liebert GXT3 8000 & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL This specification shall define the electrical and mechanical characteristics and requirements

More information

Start UP Guide. Symmetra LX Tower Rack-Mount. UPS Models 200 V, 4-8 kva 208/240 V, 4-8 kva 220/230/240 V, 4-8 kva

Start UP Guide. Symmetra LX Tower Rack-Mount. UPS Models 200 V, 4-8 kva 208/240 V, 4-8 kva 220/230/240 V, 4-8 kva Start UP Guide Symmetra LX Tower Rack-Mount UPS Models 200 V, 4-8 kva 208/240 V, 4-8 kva 220/230/240 V, 4-8 kva 200 V, 4-16 kva 208/240 V, 4-16 kva 220/230/240 V, 4-16 kva Important Safety Messages SAVE

More information

User Manual. Solar Charge Controller 3KW

User Manual. Solar Charge Controller 3KW User Manual Solar Charge Controller 3KW 1 CONTENTS 1 ABOUT THIS MANUAL... 3 1.1 Purpose... 3 1.2 Scope... 3 1.3 SAFETY INSTRUCTIONS... 3 2 INTRODUCTION... 4 2.1 Features... 4 2.2 Product Overview... 5

More information

USER MANUAL. Blazer Vista 1000/1400/2000. Uninterruptible Power System

USER MANUAL. Blazer Vista 1000/1400/2000. Uninterruptible Power System USER MANUAL Blazer Vista 1000/1400/2000 Uninterruptible Power System IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS This manual contains important instructions for model Blazer Vista 1000/1400/2000

More information

Installation and Operation Manual Back-UPS BX800CI-ZA/BX1100CI-ZA

Installation and Operation Manual Back-UPS BX800CI-ZA/BX1100CI-ZA Installation and Operation Manual Back-UPS BX800CI-ZA/BX1100CI-ZA Inventory Safety and General Information bu001c This unit is intended for indoor use only. Do not operate this unit in direct sunlight,

More information

User Manual V1.0 MaxiFlex 3000

User Manual V1.0 MaxiFlex 3000 User Manual V1.0 MaxiFlex 3000 Uninterruptible Power Supply System Table of Contents 1. Important Safety Warning 2 1-1. Transportation 2 1-2. Preparation 2 1-3. Installation 2 1-4. Operation 2 1-5. Maintenance,

More information

USER'S GUIDE. WiseHP11 SINGLE PHASE HIGH PRECISION AVR SERVO-MOTOR AUTOMATIC VOLTAGE STABILIZER

USER'S GUIDE. WiseHP11 SINGLE PHASE HIGH PRECISION AVR SERVO-MOTOR AUTOMATIC VOLTAGE STABILIZER USER'S GUIDE WiseHP11 SINGLE PHASE HIGH PRECISION AVR SERVO-MOTOR AUTOMATIC VOLTAGE STABILIZER LEN.MAN.STA.145 Rev.5.00/2010 CONTENTS 1. SAFETY INSTRUCTIONS 1 2. INTRODUCTION 2 3. FRONT PANEL AND INSIDE

More information

UPStation GXT. 6 & 10 kva 208V & 240V. USER MANUAL English

UPStation GXT. 6 & 10 kva 208V & 240V. USER MANUAL English UPStation GXT 6 & 10 kva 208V & 240V USER MANUAL English IMPORTANT SAFETY INSTRUCTIONS WARNING: Opening or removing the cover may expose you to lethal voltages within this unit even when it is apparently

More information

Valcom Failsafe Unit. 1620ESv2 SERIES. Operation and Maintenance Manual

Valcom Failsafe Unit. 1620ESv2 SERIES. Operation and Maintenance Manual Valcom Failsafe Unit 1620ESv2 SERIES Operation and Maintenance Manual Table of Contents Section Title Page 1. - Introduction.. 2. - Unpacking the Failsafe unit. 3. - Installation 3.1 - Auto / Timed UPS

More information

USER MANUAL. IPS home inverters with UPS function. IPS home inverter manual

USER MANUAL. IPS home inverters with UPS function. IPS home inverter manual USER MANUAL IPS home inverters with UPS function Suitable for UPS: - IPS300-SIN - IPS300-SIN-WM - IPS300-SIN-DC - IPS600-SIN - IPS600-SIN-WM - IPS600-SIN-DC - IPS1000-SIN - IPS1000-SIN-DC - IPS1600-SIN

More information

Liebert PowerSure PSI UPS

Liebert PowerSure PSI UPS Liebert UPS GUIDE SPECIFICATIONS 1000VA to 3000VA Single - Phase Uninterruptible Power Supply Systems 1.1 SUMMARY 1.0 GENERAL This specification defines the electrical and mechanical characteristics and

More information

Installation and user manual 5SC 500 5SC 750 5SC SC SC 500G 5SC 750G 5SC 1500G ENGLISH. Copyright 2013 EATON All rights reserved.

Installation and user manual 5SC 500 5SC 750 5SC SC SC 500G 5SC 750G 5SC 1500G ENGLISH. Copyright 2013 EATON All rights reserved. ENGLISH Installation and user manual SC 00 SC 70 SC 000 SC 00 SC 00G SC 70G SC 00G Copyright 03 EATON All rights reserved. Service and support: Call your local service representative Page IMPORTANT SAFETY

More information

USER MANUAL ONLINE UPS 6000L(XL)/10000L(XL) Uninterruptible Power Supply

USER MANUAL ONLINE UPS 6000L(XL)/10000L(XL) Uninterruptible Power Supply www.eaton.com/dxups USER MANUAL ONLINE UPS 6000L(XL)/10000L(XL) Uninterruptible Power Supply CONTENTS 1.Brief introduction 1 1.1 System and model description 1 1.2 Description of commonly used symbols

More information

Pulsar EXtreme 2200C / 3200C

Pulsar EXtreme 2200C / 3200C www.mgeups.com MGE UPS SYSTEMS Pulsar EXtreme 00C / 300C Installation and user manual P O W E R P R O V I D E R L E I B E R R U P T N T N I E U T H 3400753EN/AA - Page Introduction Thank you for selecting

More information

Online Battery Backup

Online Battery Backup Online Battery Backup UPS-1000-OL - 1000 VA UPS UPS-2000-OL - 2000 VA UPS UPS-3000-OL - 3000 VA UPS User Manual 2016 AMETEK Electronic Systems Protection / Technical Support: 1-800-645-9721 / espsurgex.com

More information

3000VA 120/208/230VAC

3000VA 120/208/230VAC User s Manual English Smart-UPS 2200VA 120/230VAC 3000VA 120/208/230VAC 2U Rack Mount Uninterruptible Power Supply 990-1352 12/02 Introduction The APC Uninterruptible Power Supply (UPS) is designed to

More information

ACC Series Power Conditioner OPERATION & INSTALLATION MANUAL

ACC Series Power Conditioner OPERATION & INSTALLATION MANUAL ACC Series Power Conditioner OPERATION & INSTALLATION MANUAL PHASETEC digital power conditioners are designed to safely operate electrical equipment in the harshest power quality environments. With a wide

More information

USER MANUAL DN / DN

USER MANUAL DN / DN USER MANUAL DN-170040/ DN-170041 Online UPS Uninterruptible Power Supply System Version:1.0 Table of Contents 1. Important Safety Warning... 1 1-1. Transportation... 1 1-2. Preparation... 1 1-3. Installation...

More information

5P 650 AU 5P 650i R 5P 850 AU 5P 850i R 5P 1150 AU 5P 1150i R 5P 1550 AU 5P 1550i R. User's guide

5P 650 AU 5P 650i R 5P 850 AU 5P 850i R 5P 1150 AU 5P 1150i R 5P 1550 AU 5P 1550i R. User's guide 5P 650 AU 5P 650i R 5P 850 AU 5P 850i R 5P 1150 AU 5P 1150i R 5P 1550 AU 5P 1550i R User's guide ENGLISH Installation and user manual Tower models 5P 650 AU 5P 850 AU 5P 1150 AU 5P 1550 AU 1U Rack models

More information

CONTENTS 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION SYSTEM DESCRIPTION OPERATION... 9

CONTENTS 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION SYSTEM DESCRIPTION OPERATION... 9 USER MANUAL 1 CONTENTS 1. INTRODUCTION... 1 2. SAFTY INSTRUCTION... 3 3. CABLE CONNECTION... 4 4. SYSTEM DESCRIPTION... 5 5. OPERATION... 9 6. TROUBLE SHOOTING GUIDE... 25 7. OPERATION MODES..... 27 8.

More information

Dycon D1532SM. EN50131/PD6662 Grade 3, 12V 2A Power Supply. Technical Description Installation and Operating Manual DYCON POWER SOLUTIONS LTD

Dycon D1532SM. EN50131/PD6662 Grade 3, 12V 2A Power Supply. Technical Description Installation and Operating Manual DYCON POWER SOLUTIONS LTD Dycon D1532SM EN50131/PD6662 Grade 3, 12V 2A Power Supply Technical Description Installation and Operating Manual DYCON POWER SOLUTIONS LTD Tel: +44 (0)1443 471 900 Unit A Cwm Cynon Business Park Mountain

More information

Dycon D2430 EN54-4 Fire Alarm Power Supply Series

Dycon D2430 EN54-4 Fire Alarm Power Supply Series Dycon D2430 EN54-4 Fire Alarm Power Supply Series Technical Description Installation and Operating Manual Construction Product Regulation 0359-CPR-00434 Page 1 of 14 Contents 1. General... 3 1.1 Product

More information

UPS USER MANUAL F-11 LINE INTERACTIVE UPS GENERAL PURPOSE UPS 650VA/1200VA/2200VA

UPS USER MANUAL F-11 LINE INTERACTIVE UPS GENERAL PURPOSE UPS 650VA/1200VA/2200VA UPS USER MANUAL F-11 LINE INTERACTIVE UPS GENERAL PURPOSE UPS 650VA/1200VA/2200VA IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS This manual contains important instructions for models Aurora Vista

More information

800VA/ 1000VA/ 1200VA/ 1500VA 2200VA/ 3000VA USER S MANUAL

800VA/ 1000VA/ 1200VA/ 1500VA 2200VA/ 3000VA USER S MANUAL U P S Uninterruptible Power System Line-Interactive Network UPS 800VA/ 1000VA/ 1200VA/ 1500VA 2200VA/ 3000VA USER S MANUAL IMPORTANT SAFETY INSTRUCTIONS IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS

More information

CONTENTS 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION SYSTEM DESCRIPTION INVERTER OPERATION...

CONTENTS 1. INTRODUCTION SAFTY INSTRUCTION CABLE CONNECTION SYSTEM DESCRIPTION INVERTER OPERATION... CONTENTS 1. INTRODUCTION...... 1 2. SAFTY INSTRUCTION.......... 2 3. CABLE CONNECTION.......... 4 4. SYSTEM DESCRIPTION............ 5 5. INVERTER OPERATION... 11 6. TROUBLE SHOOTING GUIDE....... 16 7.

More information

PR1000ELCD / PR1500ELCD User s Manual

PR1000ELCD / PR1500ELCD User s Manual PR1000ELCD / PR1500ELCD User s Manual K01-0000235-00 IMPORTANT SAFETY INSTRUCTIONS This manual contains important safety instructions. Please read and follow all instructions carefully during installation

More information

Industrial On-Line UPS V, 700 VA VA. S4KC Series. Instruction Manual

Industrial On-Line UPS V, 700 VA VA. S4KC Series. Instruction Manual Industrial On-Line UPS - 120 V, 700 VA - 3000 VA S4KC Series Instruction Manual While every precaution has been taken to ensure accuracy and completeness in this manual, Appleton Grp LLC d/b/a Appleton

More information

Pulsar Evolution 1500 / 1500 Rack 1100 / 1100 Rack 800 / 800 Rack 500 Rack

Pulsar Evolution 1500 / 1500 Rack 1100 / 1100 Rack 800 / 800 Rack 500 Rack www.mgeups.com MGE UPS SYSTEMS Pulsar Evolution 1500 / 1500 Rack 1100 / 1100 Rack 800 / 800 Rack 500 Rack Installation and user manual S T O P Y O U N O W L L W I N G I T H N O 34007117EN/AB - Page 1 Page

More information

RT Series Step Down Transformer for RT Series UPS 6-10kVA UL Input Vac Output Vac User Guide

RT Series Step Down Transformer for RT Series UPS 6-10kVA UL Input Vac Output Vac User Guide RT Series Step Down Transformer for RT Series UPS 6-10kVA UL Input 208-240 Vac Output 208-120 Vac User Guide UNLESS SPECIFICALLY AGREED TO IN WRITING, SELLER (A) MAKES NO WARRANTY AS TO THE ACCURACY, SUFFICIENCY

More information

Electrical Installation

Electrical Installation Electrical Installation Symmetra LX Tower UPS Models 200 V, 4-8 kva 208/240 V, 4-8 kva 220/230/240 V, 4-8 kva 200 V, 4-16 kva 208/240 V, 4-16 kva 220/230/240 V, 4-16 kva Important Safety Messages SAVE

More information

POWERWARE User s Guide VA.

POWERWARE User s Guide VA. POWERWARE 3110 300 700 VA User s Guide www.powerware.com FCC Part 15 Class B EMC Statements NOTE This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant

More information

USER MANUAL. Uninterruptible Power Supply Line-interactive VCL Series UPS VA

USER MANUAL. Uninterruptible Power Supply Line-interactive VCL Series UPS VA USER MANUAL Uninterruptible Power Supply Line-interactive VCL Series UPS 800 1100 2000 3000 VA GE Consumer & Industrial SA General Electric Company CH 6595 Riazzino (Locarno) Switzerland T +41 (0)91 /

More information

USER MANUAL ONLINE UPS

USER MANUAL ONLINE UPS USER MANUAL ONLINE UPS 1-3K/220Vac LCD Uninterruptible Power Systems Please comply with all warnings and operating instructions in this manual and on the unit strictly. Save this manual properly. Do not

More information

Foreword

Foreword Foreword Content 1. Summary 2. Safety instruction Safety Symbol Indication Attention Static discharge sensitive Electric shock Dangerous Indicate risk of serious injury or death or seriously damage the

More information

PREMIER POWER PACK INSTRUCTION MANUAL EN54-4 POWER SUPPLY UNIT INSTRUCTION MANUAL. GLT.MAN-138 Issue: /05/2016 N.R.P.J.

PREMIER POWER PACK INSTRUCTION MANUAL EN54-4 POWER SUPPLY UNIT INSTRUCTION MANUAL. GLT.MAN-138 Issue: /05/2016 N.R.P.J. EN54-4 POWER SUPPLY UNIT INSTRUCTION MANUAL GLT.MAN-138 CONTENTS Introduction to the Premier Power Pack PSU... 2 Changes to EN54-4 (The Fire Alarm Equipment Power Supply Standard)... 3 Indications... 4

More information

Matrix APAX. 380V-415V 50Hz TECHNICAL REFERENCE MANUAL

Matrix APAX. 380V-415V 50Hz TECHNICAL REFERENCE MANUAL Matrix APAX 380V-415V 50Hz TECHNICAL REFERENCE MANUAL WARNING High Voltage! Only a qualified electrician can carry out the electrical installation of this filter. Quick Reference ❶ Performance Data Pages

More information

Uninterruptible Power Supply

Uninterruptible Power Supply AC/DC Din Rail UPS System Single Phase Input, Single Phase Output Uninterruptible Power Supply 600VA UPS System AC/DC Din Rail Mount Line Interactive (PWM): 600VA User Manual M1201_Din_Rail_AC-DC_600VA_Manual

More information

Liebert PowerSure PSI

Liebert PowerSure PSI Power Protection for Business Critical Continuity Liebert PowerSure PSI User Manual 1000-3000VA, 60 Hz, 120V TABLE OF CONTENTS IMPORTANT SAFETY INSTRUCTIONS................................................1

More information

Liebert GXT & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS

Liebert GXT & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.1 SUMMARY Liebert GXT4 8000 & 10000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL This specification shall define the electrical and mechanical characteristics and requirements

More information

5 IN 1 JUMP START OPERATION & MAINTENANCE INSTRUCTIONS MODEL NO: JS5IN1 PART NO: LS0810

5 IN 1 JUMP START OPERATION & MAINTENANCE INSTRUCTIONS MODEL NO: JS5IN1 PART NO: LS0810 5 IN 1 JUMP START MODEL NO: JS5IN1 PART NO: 6240005 OPERATION & MAINTENANCE INSTRUCTIONS LS0810 INTRODUCTION Thank you for purchasing this CLARKE product. Before attempting to use this product, please

More information

Centurion 1000/1500/2000/3000 Tower/Rackmount On Line UPS User s manual

Centurion 1000/1500/2000/3000 Tower/Rackmount On Line UPS User s manual Centurion 1000/1500/2000/3000 Tower/Rackmount On Line UPS User s manual www.powershield.com.au 0 Introduction Thank you for choosing PowerShield. PowerShield Centurion UPS series are designed to provide

More information

General Precautions. Personnel Precautions

General Precautions. Personnel Precautions USER MANUAL General Precautions 1. Before using Inverex, read all instructions and cautionary markings on : (1) Inverex (2) the batteries (3) this manual 2. CAUTION --To reduce risk of injury, charge only

More information

User Manual Back-UPS BC500-RS, BC650-RS 650 VA 230 V

User Manual Back-UPS BC500-RS, BC650-RS 650 VA 230 V User Manual Back-UPS BC500-RS, BC650-RS 650 VA 230 V Important Safety Information Read the instructions carefully to become familiar with the equipment before trying to install, oate, service or maintain

More information

USER MANUAL. PowerMust 1080 LCD (1KVA), Online, IEC PowerMust 2016 LCD (2KVA), Online, IEC PowerMust 3024 LCD (3KVA), Online, IEC

USER MANUAL. PowerMust 1080 LCD (1KVA), Online, IEC PowerMust 2016 LCD (2KVA), Online, IEC PowerMust 3024 LCD (3KVA), Online, IEC USER MANUAL PowerMust 1080 LCD (1KVA), Online, IEC PowerMust 2016 LCD (2KVA), Online, IEC PowerMust 3024 LCD (3KVA), Online, IEC CONTENT 1. Safety and EMC Instructions... 1 1.1 Installation... 1 1.2 Operation...

More information

USER MANUAL. PowerMust 1400/2000 LCD. Uninterruptible Power System

USER MANUAL. PowerMust 1400/2000 LCD. Uninterruptible Power System USER MANUAL PowerMust 1400/2000 LCD Uninterruptible Power System IMPORTANT SAFETY INSTRUCTIONS SAVE THESE INSTRUCTIONS This manual contains important instructions for model Power Must 1400/2000 LCD that

More information

Model ESV Uninterruptible Power System 1.5 KVA/KW KVA/KW Single Phase

Model ESV Uninterruptible Power System 1.5 KVA/KW KVA/KW Single Phase Model ESV Uninterruptible Power System 1.5 KVA/KW - 14.0 KVA/KW Single Phase 1.0 General General Specification This specification describes the features and design of an on-line, dual conversion, uninterruptible

More information

Solar Hybrid Power Generating System CPS1200EOH12SC CPS2200EOH24SC CPS3000EOH24SC. User s Manual K01-C

Solar Hybrid Power Generating System CPS1200EOH12SC CPS2200EOH24SC CPS3000EOH24SC. User s Manual K01-C Solar Hybrid Power Generating System CPS1200EOH12SC CPS2200EOH24SC CPS3000EOH24SC User s Manual K01-C000304-02 2 TABLE OF CONTENTS 1 IMPORTANT SAFETY INSTRUCTIONS..4 2 INSTALLATION....5 2-1 Unpacking...5

More information

Power Inverter. User s Manual. Diamond Series CPD1200EILCD

Power Inverter. User s Manual. Diamond Series CPD1200EILCD Power Inverter Diamond Series CPD1200EILCD User s Manual 2 TABLE OF CONTENTS 1 IMPORTANT SAFETY INSTRUCTIONS..4 2 INSTALLATION....5 2-1 Unpacking...5 2-2 Product Overview & Outlook..5 2-3 Power Requirements

More information

User s Manual. Automatic Switch-Mode Battery Charger

User s Manual. Automatic Switch-Mode Battery Charger User s Manual Automatic Switch-Mode Battery Charger IMPORTANT Read, understand, and follow these safety rules and operating instructions before using this battery charger. Only authorized and trained service

More information

User Manual 1KVA-5KVA INVERTER / CHARGER

User Manual 1KVA-5KVA INVERTER / CHARGER User Manual 1KVA-5KVA INVERTER / CHARGER Version: 1.7 Table Of Contents ABOUT THIS MANUAL... 1 Purpose... 1 Scope... 1 SAFETY INSTRUCTIONS... 1 INTRODUCTION... 2 Features... 2 Basic System Architecture...

More information

USER MANUAL. Uninterruptible power supply MODEL: 53965,

USER MANUAL. Uninterruptible power supply MODEL: 53965, USER MANUAL Uninterruptible power supply MODEL: 53965, 53966 www.qoltec.com Please check if the package contains: - UPS unit - Power cable (1 x SCHUKO) 1.2 m - User manual This UPS provides comprehensive

More information

CP900EPFCLCD User s Manual K

CP900EPFCLCD User s Manual K CP900EPFCLCD User s Manual K01-0000190-00 IMPORTANT SAFETY INSTRUCTIONS This manual contains important safety instructions. Please read and follow all instructions carefully during installation and operation

More information

USER MANUAL English / Español

USER MANUAL English / Español UPStation GXT LRT TM Battery Cabinet for use with the 1800-3000 VA UPS Units USER MANUAL English / Español IMPORTANT SAFETY INSTRUCTIONS WARNING: Do not attempt to service this product yourself. Opening

More information

Installation and Operation Manual Back-UPS BX1100CI-CN

Installation and Operation Manual Back-UPS BX1100CI-CN Installation and Operation Manual Back-UPS BX1100CI-CN Safety and General Information This unit is intended for indoor use only. Do not operate this unit in direct sunlight, in contact with fluids, or

More information

Informer Compact Series

Informer Compact Series IMPORTANT SAFETY INSTRUCTIONS Informer Compact Series LINE-INTERACTIVE SINEWAVE UPS Uninterruptible Power System WARNING : (SAVE THESE INSTRUCTIONS) This manual contains important safety instructions.

More information

Table of Contents 文管中心 發行章

Table of Contents 文管中心 發行章 ST600-XXX Series Pure Sine Wave Power Inverter User s Manual Table of Contents 1. Important Safety Instructions 1-1 General Safety Precautions 1 1-2 Battery Precautions. 1 2. Basic Descriptions 2-1 Mechanical

More information

XPRT 6kVA & 10kVA Online UPS

XPRT 6kVA & 10kVA Online UPS For more information, visit www.247technology.com/single-phaserackmounttower-ups/xtreme-power-conversion-xprt-6-10 XPRT 6kVA & 10kVA Online UPS 6kVA, 10kVA Models User & Installation Manual 2015. All rights

More information

Liebert GXT2-6000RTL630

Liebert GXT2-6000RTL630 AC Power For Business-Critical Continuity Liebert GXT2-6000RTL630 User Manual - 208 / 240 VAC TABLE OF CONTENTS IMPORTANT SAFETY INSTRUCTIONS..........................................1 GLOSSARY OF SYMBOLS.......................................................3

More information

Installation and Operating Instructions. MPPT Solar System Controller ISC3040

Installation and Operating Instructions. MPPT Solar System Controller ISC3040 Installation and Operating Instructions MPPT Solar System Controller ISC3040 ABOUT THIS MANUAL These operating instructions come with the product and should be kept with it as a reference to all user s

More information

Liebert GXT & 6000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL

Liebert GXT & 6000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL 1.1 SUMMARY Liebert GXT4 5000 & 6000VA RT208 Rack-Tower models, Dual Inverter GUIDE SPECIFICATIONS 1.0 GENERAL This specification shall define the electrical and mechanical characteristics and requirements

More information

User Manual Back-UPS BX650CI-MS 230 Vac with AVR

User Manual Back-UPS BX650CI-MS 230 Vac with AVR User Manual Back-UPS BX650CI-MS 230 Vac with AVR Overview Safety and General Information Inspect the package contents upon receipt. Notify the carrier and dealer if there is any damage. Read the Safety

More information